100 m - wow. Have you measured the voltage that the kiln actually receives when it is running???Oldfoundryman is my favourite. I,ve spent quite a few hours watching his videos. And there is lots of little details to pick up. I plan to stay clear of both fluxes and degassers etc for now. Keep it simple. This time I got closer to getting the gating right(copying olfoundryman) while the temperatures were all over the place. I use a electric kiln that is dead slow and a 100m cord does not help.
I have not done that yet. The cable is 2,5mm2 but the kiln takes at least 30min to get to temperature so there is a considerate voltage drop. My mig welder works fine though.100 m - wow. Have you measured the voltage that the kiln actually receives when it is running???
At least two things yes. Thats life..Yeah ouch Reidar! :S
But hay you learnt at least 2 x new things!
You intend to get the moulds 3D printed and cast from them?
Hi COL. The kiln is 1900W/220V. Is it within limits or far out?What is current draw or the Kw rating of your kiln Reidar? I assume your voltage supply there is 220 volts.
Surprise its within limits which is 5% here in Australia.Hi COL. The kiln is 1900W/220V. Is it within limits or far out?
I used an online calculator as I couldn't be bothered to go and look up what we use here so maybe the calculator that i used was not correct.Regarding voltage drop, you would need a cable to have less than 12.73 mV/Am ( milli volts per Ampere Metre) to be within the Australian standard of a maximum 5% voltage drop using your voltage and current draw and length of run. A 4 sqmm flexible lead is just outside this at 13 mV/Am.
By comparison, and certainly there is some overkill in the 30 metre 3 phase run to my shed in 10 sq mm. Yes, I am an electrician.
Seems we have some differing maths. I have the circuit using a 2.5mm lead (18mV/Am) 100m long having a 15.53v drop at 8.64A (1900W divided by the 220V supplied) load so coming in at just over a 7% voltage drop currently. Happy to be proved wrong. Can’t say I do the calculations for this very often, but believe I am correct.
When I did the calculations using AS3008.1.1 I got the same as you AlanRegarding voltage drop, you would need a cable to have less than 12.73 mV/Am ( milli volts per Ampere Metre) to be within the Australian standard of a maximum 5% voltage drop using your voltage and current draw and length of run. A 4 sqmm flexible lead is just outside this at 13 mV/Am.
By comparison, and certainly there is some overkill in the 30 metre 3 phase run to my shed in 10 sq mm. Yes, I am an electrician.
Seems we have some differing maths. I have the circuit using a 2.5mm lead (18mV/Am) 100m long having a 15.53v drop at 8.64A (1900W divided by the 220V supplied) load so coming in at just over a 7% voltage drop currently. Happy to be proved wrong. Can’t say I do the calculations for this very often, but believe I am correct.
That is a good question but a highly hypoteticly one as there have been about 4-5days of snow the last couple of years. I hope that is a coincidence.how would it effect your voltage drop calk if cable was berried in snow ,Norway